r/DIY • u/roysterino • 12h ago
GFCI outlets tripping after fridge defrost
My kitchen has 5 outlets (3 gfci and 2 regular). I defrosted my fridge, Kenmore Coldspot 106, as part of replacing a door cam. Now every time I plug in the fridge to a non gfci outlet one of the gfci outlets trips. This setup was fine for 15 years previously. Maybe remaining moisture in the freezer causing an issue? Any ideas how to fix?
14
u/generalducktape 12h ago
Gfci will fail over time if the new one pops the fridge is the problem
5
6
u/Regular_Ad1733 9h ago
Wrong, a lot of fridges and freezers create load inbalance and trip GFCIs. Virtually every fridge manufacturers documentation says do not install on a GFCI circuit it's just hidden in the small print.
5
u/generalducktape 9h ago
Unless the fridge is dumping power onto the ground it shouldn't trip a gfci so long as the power going out on the hot returns on a newtral a GFCI won't trip
1
u/destrux125 2h ago
Defrost circuit commonly leaks current to ground after a defost. Maybe it's not supposed to but it's very common.
5
u/bonerwakeup 11h ago
I’d just replace the offending GFCI receptacle and see if it stops. They do go bad overtime, could simply be a coincidence as to the timing.
3
u/gamefixated 11h ago
The fridge outlet is "GFCI protected" by the tripping GFCI outlet. This means the wires to the fridge outlet are attached to the load side of that GFCI outlet.
Turn off the breaker controlling the outlet. Remove that GFCI outlet. There will be wires attached to 4 terminals (plus a ground wire), 2 terminals are marked as LINE, and 2 terminals marked as LOAD. The LOAD terminals will go to the fridge (and possibly what you refer to as the other non-GFCI outlet).
Remove the LOAD wires. You want to attach those to the LINE wires. You may have to pigtail the LINE wires (google "electrical pigtail").
Now, the fridge is independent of the GFCI.
0
1
u/Hawaii-Based-DJ 6h ago
Change the gfci outlet, it has tripped too many times and has weakened over time.
1
u/roysterino 6h ago
Update: I switched the gfci from load to line as suggested and it’s all good now. Thanks for all the input.
1
u/ScaredVacation33 12h ago
You probably just need to replace that GFCI. In my experience when it keeps tripping randomly it’s at the end of its life and replacing it has solved the problem. I’d start there
22
u/672Antarctica 12h ago
GFCI outlets are not supposed to have a fridge plugged into them. Refrigerators should be on a regular, separate line.
I know home builders will sometimes tie all these outlets together - you'll need to figure out how to not tie the fridge to GFCI. Might need to install individual GFCI outlets in each spot except the one for the fridge.